air-to-air HVAC loop

asked 2017-02-24 06:55:52 -0600

sga's avatar

I have created the following airloop, but I get this error: * Severe * IP: IDF line~4297 Object=CONTROLLER:MECHANICALVENTILATION, name=CONTROLLER MECHANICAL VENTILATION 1, Required Field=[Zone 1 Name] was blank. How and where can I fix that? I have checked some other posts about this issue, and things like design days and design specification outdoor air seems to be fine.

image description

edit retag flag offensive close merge delete

Comments

Adam Hilton's avatar Adam Hilton  ( 2017-02-24 08:27:05 -0600 )edit

You also don't have any terminal equipment. You need something to connect the splitter to the zones.

Adam Hilton's avatar Adam Hilton  ( 2017-02-24 08:28:15 -0600 )edit

I have checked the question and I do not think any of the 5 errors mentioned occur in my file... How can I connect the splitter to the zones?

sga's avatar sga  ( 2017-02-26 13:57:18 -0600 )edit

Add an air terminal prior to the zone.

Adam Hilton's avatar Adam Hilton  ( 2017-02-26 15:00:47 -0600 )edit

I have added air terminal now, and the the analysis runs. However, I do not think it has any result on the temperature/humidity. Will this HVAC system warm up the incoming air by using the exhaust air (at least to some extend) and how do I set for example the temperature ranges I want to have? Lets say I want the temperature inside to be between 18 and 22 degrees. Thank you

sga's avatar sga  ( 2017-02-27 16:56:34 -0600 )edit