Using Airflow Network with Ideal HVAC load system?
My building has operable windows and single zone split HVAC for heating and cooling. I have set up a Airflow Network in energyplus to find out how natural ventilation can contribute to lower cooling loads. (Location: mixed humid climate and mixed dry climate, ASHRAE 4A and 4B).
However, I get strange results for the winter period because natural ventilation is happening while heating is ON.
What is the right approach to avoid this? Might it be that the IdealLoadAirSystem is not interacting correctly with the AirFlowNetwork Model. Or should I set up a schedule to avoid ventilation in winter nights?
I found this information in energyplus documentation (but not sure which HVAC system does it mean): The AirflowNetwork model is currently able to model a wide range of multizone air flow scenarios. However, only a single air distribution system with a constant volume supply fan can be included as part of the airflow modeling.
@MJWitte or @Archmage, could you, please give me some insight view on the compatibility of air flow network and HVAC objetcs. Actually, I was thinking to use ideal loads because I am not interested in HVAC details.
The objective of my simulation is to find out best passive design strategies to reduce heating and cooling loads. My location is in Nepal and I have no data about actual infiltration rates, etc. I am doing parametric analysis with jEPlus; so I run a high number of simulations.
I haven't done natural ventilation in E+ (IESVE), but how are you governing the opening/closing of the windows? They will at least be governed by both the ambient (outside) temp and the inside space temp(s), with respect to your setpoint(s).
Yes. I have set up a ventilation setpoint (24C) in energyplus. That means when indoor temp goes above this setpoint the windows are opened. What happens in winter is that the heating system somehow drives ambient temperature above 24 and, thus, windows are opened. In energyplus I cannot set up a limit for outdoor temperature:-(
Aside from possible incompatibility between Airflow Network and IdealLoadAirSystems, could you not use an EnergyPlus Energy Management System routine to control window opening based on outdoor as well as indoor temperature?
@Eric Ringold. Thanks for EMS hint. I did some trial with HybridVentilation and it seems to work properly.
However, are you sure that Airflow Network and IdealLoadAirSystems are incompatible? I did not find any info on that in e+ documentation.
Oh no, I'm not at all sure about that. I meant that I couldn't speak to that part of your question. Sorry for the confusion.