Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Humidity Control in Detailed HVAC

asked 2017-01-30 09:20:32 -0500

updated 2017-05-03 20:55:49 -0500

When Using the Detailed HVAC do we need to add a humidifier to the Air Handling Unit? Does the software not automatically take the humidity set points from the Activity set?

Humidity in Activity Tab

Problem is when I am changing the RH Humdification and Dehumidification set points the results are not giving any changes in energy.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2017-01-30 09:54:24 -0500

Vmoreno's avatar

It depends of the programation on Model Options. If you designate Detailed HVAC and Option 2-Detailed HVAC Data in Detailed HVAC Activity data, the (Des)Humidification setpoint used are the setpoints in HVAC Zone. Otherwise, if you designate Option 1-Simple HVAC Data in Detailed HVAC Activity data, the (Des)Humidification setpoint used are the setpoints in Activity Data. You have to model (Des)Humidification process in AHUs modeled.

I recommend you seeing this text:

https://www.designbuilder.co.uk/helpv...

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2017-01-30 09:20:32 -0500

Seen: 354 times

Last updated: Jan 30 '17