Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Design cooling load for radiant slab

asked 2017-01-06 11:22:13 -0500

ptruong's avatar

updated 2017-05-08 18:34:39 -0500

Hello, I am modeling an active slab (in EnergyPlus 8.5) and need to determine the peak sensible cooling load. Currently, I am not including any ventilation, just sensible loads. In the output reports (i.e. Component Sizing Summary or "Peak Design Sensible Load" under Zone Component Load Summary), the reported peak loads match. However, when I look at the variables output for the design day condition (day and time) specified as peak in the output reports, the "Zone Radiant HVAC Cooling Rate" does not match. What is the difference between this value and the one reported in the output reports?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
0

answered 2018-02-11 07:30:40 -0500

Siva's avatar

the one that you had seen in the component sizing summary is the maximum capacity of the system and hence when you did the simulation, the peak value should not be more than that and the peak value of simulation matches with the one in design....

Coming to the when I look at the variables output for the design day condition (day and time) specified as peak in the output reports, the "Zone Radiant HVAC Cooling Rate" does not match.

the reason is simulation consider the previous day load profile while design does not do that....it is because of this, the difference exists

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

Stats

Asked: 2017-01-06 11:22:13 -0500

Seen: 216 times

Last updated: Feb 11 '18