Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
5

VAV Reheat Coil Sizing

asked 2016-12-12 22:32:10 -0600

sspielman's avatar

updated 2017-08-28 09:19:31 -0600

I am having a problem with heating unmet hours on a VAV system that appears to be an issue with the reheat coil. The problem only occurs in internal zones where the heating load on the coil is due to reheat only. On exterior spaces where there is envelope load there is not problem. The issue is most obvious in large spaces where ACH are high compared to internal loads. The VAV box is supplying air near 55F and not reheating to meet the temperature setpoint. It appear that the coil is not being sized for the reheat load and only for whatever exterior load exists which is none.

Here is my sizing:zone object C:\fakepath\Capture.PNG

Here is my sizing:system object C:\fakepath\Capture1.PNG

The loop set up is simple with a HW loop operating at 130F with a 40F delta T serving the air loop.

Does anyone have insight into why the coil is being sized incorrectly and I am seeing unmet hours?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
6

answered 2016-12-14 07:29:07 -0600

Archmage's avatar

This is fairly common issue. The zone's design heating load is used to size the reheat coil and if that load is tiny or zero the reheat coils do not come out with enough capacity.

One way of getting some design heating load is to use OtherEquipment (now with the fuel type set to None) with a negative value for the power. A negative internal gain will provide cooling to the zone and thus a design heating load. I use something lik e -20.0 W/m2 or so. Use the OtherEquipment schedule so that the loads occur only during heating design days by using the day type called WinterDesignDay.

edit flag offensive delete link more

Comments

1

Thank you for the feed back. I guess the work around is providing a dummy load in the space on the heating design day. Is there no way to include a minimum ventilation reheat load on the heating design day?

sspielman's avatar sspielman  ( 2016-12-14 13:52:21 -0600 )edit

@Archmage, I tried to add the negative other equipment definitions, it seems it is only allowed to add "Design Level" with unit "W", but not "Energy Per Space Floor Area" with unit "W/m2"?

Yan's avatar Yan  ( 2016-12-20 15:25:43 -0600 )edit

@Yan, the field you are looking for would be "Power per Zone Floor Area". I see this as an input in EnergyPlus v8.5.

@Archmage, what would the schedule:compact object look like exactly, to only have the schedule apply on heating days? Something like this?

Schedule:Compact, Other Equipment Schedule, Fraction,
Through: 12/31,
For: WinterDesignDay,
Until: 24:00,
1,
For: AllOtherDays,
Until: 24:00, 0;

JustinLueker's avatar JustinLueker  ( 2017-03-13 11:25:45 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

2 followers

Stats

Asked: 2016-12-12 22:32:10 -0600

Seen: 2,614 times

Last updated: Dec 14 '16