Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

100% Relative Humidity and Condensation during Summer in a Residential Model?

asked 2016-11-13 21:29:56 -0500

zach.alderman's avatar

updated 2016-11-14 11:50:56 -0500

Hi Everyone, I am using OS for a research project (graduate level, not a homework assignment or class project) looking at thermostat setbacks in single family detached residential homes. The issue I am currently running into is that running fixed infiltration rates of .35 or 0.5 ACHnat (to match the real homes we are reflecting) my model is telling me that with the setbacks and occupancy schedules I have, there are large portions of time (2000+ hours) where my humidity levels are above 80% RH, and over 200 hours where it is over 98% based on zone relative humidity.

I am running a custom weather file that runs a "design week" for half the year in heating mode and half the year in cooling mode to test numerous control schemes over the course of the year in one model and compress the number of simulations I need to do, and this is only an issue during cooling season where the zone temp only trips the AC on for ~100 hours over the 6 month period. I have the opposite issue (extremely low RH) in the winter but the heat is active a significant amount of the time so I can understand with dry cold constant infiltration how then heating that air would lower the RH in the zone. My concern is that on the summer side having 200+ hours of "rain" inside is completely unrealistic and therefore I may not be modeling it properly. Since it is happening every week the issue appears to be independent of my various setback control schemes.

I understand I can force dehumidification with a Zone:humidistat and associated schedule and dehumidifier but I want to stay true to a traditional existing residential HVAC system which does not typically possess such a mode, and I am still concerned there is something else in my model that needs checking. As a thought exercise I did integrate a dehumidifier and run it in two models. One kept all of my original thermostat, occupancy, and load schedules, and the second (which I'll refer to as the 68 Model) kept occupancy and load schedules but changed the thermostat setpoint to a constant 68F for all cooling times. Both dehumidifiers were set to maintain RH <=70%. While the first model dehumidifier only ran ~150 hours longer (1068 hours v 916) than the 68 model, it removed 7.8 times the water by mass, and consumed 7.8 time the electricity by energy consumption. That makes sense since in the 68 model the cooling coil was on a significantly large percentage of the cooling season so it was able to reduce the amount of supplemental dehumidification needed. However given supplemental was still needed even in the 68 model where in a typical home it wouldn't be, I am still concerned that I am not properly modeling either my vapor/latent loads, or my infiltration (could of course be something else too!).

I am not running any outdoor air ... (more)

edit retag flag offensive close merge delete

2 Answers

Sort by ยป oldest newest most voted
2

answered 2016-11-14 08:26:21 -0500

What schedules and magnitudes are you using for latent gains? I would start by comparing them to something like the Building America House Simulation Protocols.

Is there an OS variable that I can use to determine how much vapor is coming into the space through infiltration?

I believe there is an EnergyPlus output variable for that ("Zone Infiltration Latent Gain" or something like that). Check the .rdd file.

edit flag offensive delete link more

Comments

Eric thank you for starting this processs. I built all of my internal load schedules except thermostat setback points and occupancy state schedules to match the building America 2014 protocol. The thermostat and occupancy schedules are the crux of my research focus and I'd prefer to keep them private. I am in fact reporting the zone infiltration latent gain, as well as latent loss in the winter, which is giving me energy but I'm struggling to convert that into a mass of water introduced or lost. More of a physics/thermo problem but if someone can remind me how to get there it would be great.

zach.alderman's avatar zach.alderman  ( 2016-11-14 09:29:45 -0500 )edit
1

The latent heat of evaporation of water = 2257 kJ/kg. The report variable Zone Infiltration Latent Heat Gain Energy is in Joules. Divide Zone Infiltration Latent Heat Gain Energy by the latent heat of evaporation of water and then by 1000 to get kg.

rraustad's avatar rraustad  ( 2016-11-14 10:00:19 -0500 )edit

Yep...should have thought of that. Sometimes it's good to let someone else remind you about the basics. Thank you!!

zach.alderman's avatar zach.alderman  ( 2016-11-14 10:11:03 -0500 )edit
1

@zach.alderman, you might also check the sensible heat ratio (SHR) of your AC (both input/rated and output).

Eric Wilson's avatar Eric Wilson  ( 2016-11-14 11:17:27 -0500 )edit

@Eric Wilson where would I find that? I left it to auto size on HVAC equipment, and it isnt showing up in either the Openstudio or Energyplus Results summaries.

zach.alderman's avatar zach.alderman  ( 2016-11-14 15:08:53 -0500 )edit
2

answered 2017-03-09 16:07:52 -0500

brianbergNZ's avatar

This answer is probably too late, however I have just encountered and solved a similart issue.

Are you using the advanced moisture modelling algorithmns in the HeatBalanceAlgorithm Object?

I had the same problem, because my materials were not absorbing and then releasing water. It is called buffering. The easiest way is to use the EMPD Effective Moisture Penetration Depth model. EP8.6 as just had these significantly improved, and NREL and Oak Ridge have been very active in this area the last two years.

edit flag offensive delete link more

Comments

Thanks very much!! Not too late fortunately. Can you walk me through what using the EMPD model entails? Does it require using specific materials? Thanks very much, I'm so excited to try this out!

zach.alderman's avatar zach.alderman  ( 2017-03-09 18:46:23 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

2 followers

Stats

Asked: 2016-11-13 20:58:38 -0500

Seen: 482 times

Last updated: Nov 14 '16