EIR Chiller Performance Factors

asked 8 years ago

Matt Koch's avatar

updated 8 years ago

I have studied the definitions of ChillerCapFTemp, ChillerEIRFTemp and ChillerEIRFLR and have reached a point where I believe ChillerEIRFPLR may not be defined correctly? I have summarized my findings in a PDF document, but I noticed I cannot post this here. So I exported to three PNG files instead, which are attached.

image description

image description

image description

I hope they will be legible, and I apologize for the length, but I thought I'd try to be as clear about my thoughts as possible. I'd appreciate any advice.

Preview: (hide)

Comments

I was just curious if anyone might have had a chance to review the above? I apologize for the complexity of the presentation, but do not know how else to make my question as clear as I possibly can. Or is all of this going to go away in OpenStudio 2.1?Thanks.

Matt Koch's avatar Matt Koch  ( 8 years ago )

1 Answer

Sort by » oldest newest most voted
3

answered 8 years ago

See if this helps:

image description

Preview: (hide)
link

Comments

Update: Correct equation for ChillerEIRfPLR is available in the Engineering Reference document up to V8.4.

rraustad's avatar rraustad  ( 8 years ago )

Where do you see in the documentation that the definition of f3 is EIRact/EIRcap ? Or is it simply your translation of the variable name?

rraustad's avatar rraustad  ( 8 years ago )

Two thoughts:

1) Your explanation seems to confirm that ChillerEIRFPLR is indeed equal to what I refer to as bar(f)3.

2) My definition of f3, i.e. NOT bar(f)3, is based on: "The output of this curve is multiplied by the reference EIR (inverse of the reference COP) and the Energy Input to Cooling Output Ratio Function of Temperature Curve to give the EIR at the speicfic temperature and part-load ratio at ehich the chiller is operating." (http://bigladdersoftware.com/epx/docs...).

Matt Koch's avatar Matt Koch  ( 8 years ago )

so, further to item 2): EIRref = Pref/Qref, EIRact = Pact/Qact, ChillerEIRFTemp = EIRcap/EIRref, where I am assuming that ChillerEIRFTemp is the "Energy Input to Cooling Output Ratio Function of Temperature Curve" of the above definition. Therefore, ChillerEIRFPLR * EIRref * ChillerEIRFTemp = EIRact, or ChillerEIRFPLR * EIRref * EIRcap/EIRref = EIRact. Hence: ChillerEIRFPLR = EIRact/EIRcap, which is my definition of f3.

Matt Koch's avatar Matt Koch  ( 8 years ago )

so, I am thinking if your derivation from the EnergyPlus Engineering reference is indeed on target, then perhaps all that needs to e changed is the verbal definition in http://bigladdersoftware.com/epx/docs....

Matt Koch's avatar Matt Koch  ( 8 years ago )