ground heat exchanger double-u boreholes

asked 2016-11-04 10:22:05 -0600

Diego's avatar

updated 2017-05-05 10:15:48 -0600

Can I simulate a geothermal field with double-u boreholes in OpenStudio, without use of GLHEPro? I alredy know the proprieties of the ground and the borehole (tube and grout) and also the g-function of the field.

If I put this values in OS:GroundHeatExchanger:Vertical and I run the simulation, it give me this error: Severe ** Plant temperatures are getting far too cold, check controls and relative loads and capacities.

This is the condenser loop. On the right, you can see some parameters of the borehole; others values are: Pipe out diameter: 0.032 m; U-tube distance: 0.0505 m; Pipe thickness: 0.003 m. I used a "setpoint manager schedule" on the outlet node of the supply side that imposes a temperature of 6°C. Also, you can see here the output error: image description

edit retag flag offensive close merge delete

Comments

Please tag each question with the software you are using, e.g., 'openstudio' and 'glhepro' in this case.

__AmirRoth__'s avatar __AmirRoth__  ( 2016-11-04 10:30:03 -0600 )edit

Sounds like you have the ground loop running continuously or have the setpoint controls wrong. Could you update your question to describe the controls you are using and a screenshot of the loop(s) involved?

aparker's avatar aparker  ( 2016-11-04 13:47:56 -0600 )edit