Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

How can I set the unmethours range in OS?

asked 2016-10-21 08:57:06 -0600

poppo92's avatar

updated 2016-10-21 10:32:34 -0600

In openstudio I run the simulation and I see the unmethours. But what is the range of the software? Where can I see and define the range?

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
3

answered 2016-10-21 09:29:18 -0600

gokul's avatar

updated 2016-10-21 09:30:27 -0600

image descriptionHi, I don't think there is a way to specify if the simulation should terminate if the number of unmet hours goes beyond a specified value.(If that was your question?) Since the simulation is performed annually, the number of unmet hours can range from 0 to 8760, on both the cooling and heating side. You can, however, specify a tolerance limit for the temperature difference above and below the zone setpoint temperatures, which OpenStudio uses for calculating unmet hours. This is done in the Output Control Reporting Tolerances sub-tab under the Simulation tab (shown in figure.) If you are interested in reducing unmet hours, the first step would be to figure out which of your zones have unmet hours and whether these occur during cooling or heating. The Time Setpoint Not Met report under the System summary in the energyplus output file would give you the unmet hours by zone. You would then go about reducing unmet hours. There are numerous posts on how to do this depending on the issue on unmet hours. https://unmethours.com/question/359/w... maybe a good place to start. Hope this answers your question.

edit flag offensive delete link more

Comments

sorry, my question wasn't totally correct. I was meaning the range of temperature of the unmethours. I would like to see and change the range of temperature, for excample 20-26 C°, or 22-26 C°..is it possible? thank you

poppo92's avatar poppo92  ( 2016-10-21 11:10:08 -0600 )edit
1

You can assign different heating and cooling setpoint schedules using the thermal zones tab. If you would rather alter the existing schedules, then use the Schedules tab.

David Goldwasser's avatar David Goldwasser  ( 2016-10-21 11:16:29 -0600 )edit

ok..anyway my building has no HVAC system, because thickness of walls is very high. Is it possible to have unmethours output even if I don't have HVAC?

poppo92's avatar poppo92  ( 2016-10-21 15:31:59 -0600 )edit

@poppo92, you can still have thermostats even if you don't have an HVAC system serving it. I believe in that case unmet hours will still be reported.

David Goldwasser's avatar David Goldwasser  ( 2016-10-21 15:50:12 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2016-10-21 08:57:06 -0600

Seen: 657 times

Last updated: Oct 21 '16