Thank you very much your comment is right but am still getting errors any idea why?
First time here? Check out the Help page!
The ELSEIF doesn't make sense. If AvailSCH_Overwrite = 0 && something else, SET AvailSCH_Overwrite = 0 ??
IF AptTemp > (hSP), SET AvailSCH_Overwrite = 0,
ELSEIF AvailSCH_Overwrite == 0 && AptTemp >= (hSP) && AptTemp <= (hSP + Toffset), SET AvailSCH_Overwrite = 0,
ELSE, SET AvailSCH_Overwrite = 1, ENDIF
The program should instead do:
IF AvailSCH_Overwrite == 0 && AptTemp < (hSP), SET AvailSCHOverwrite == 1,
ELSEIF AvailSCH_Overwrite == 1 && AptTemp > (hSP+Toffset), SET AvailSCHOverwrite == 0,
ELSE SET AvailSCHOverwrite == NULL;
Thank you very much your comment is right but am still getting errors any idea why?
If this question is related to the linked one than you need first to set the heating setpoint to 26C and an EMS control logic will be similar to the code desribred here
This is the code which should work in your case
Schedule:Constant,Cycle,OnOff,1; ! New schedule object
AvailabilityManager:Scheduled, ! Updated Availability Manager
Packaged Rooftop Air Conditioner Availability Manager,
Cycle;
EnergyManagementSystem:Sensor,
AptTemp,
BLOCK1:ZONE1,
Zone Mean Air Temperature;
! Don't forget to set heating setpoint to 26C
EnergyManagementSystem:Sensor,
hSP,
BLOCK1:ZONE1,
Zone Thermostat Heating Setpoint Temperature;
EnergyManagementSystem:Actuator,
AvailSCH_Overwrite,
Cycle,
Schedule:Constant,
Schedule Value;
EnergyManagementSystem:ProgramCallingManager,
Supervision,
BeginTimestepBeforePredictor,
HVAC_uncontolledloop_Supervision;
EnergyManagementSystem:Program,
HVAC_uncontolledloop_Supervision,
SET Toffset = 4,
IF AptTemp > (hSP - 0.01), ! -0.01 due to system can maintain the zone temperature very close to the setpoint
SET AvailSCH_Overwrite = 0,
ELSEIF AvailSCH_Overwrite == 0 && AptTemp >= (hSP - Toffset),
SET AvailSCH_Overwrite = 0,
ELSE,
SET AvailSCH_Overwrite = 1,
ENDIF;
Please start posting anonymously - your entry will be published after you log in or create a new account.
Asked: 2016-10-19 07:16:41 -0600
Seen: 815 times
Last updated: Oct 20 '16
Are 22C and 26C your heating and cooling setpoints?
I said the ELSEIF doesn't make sense because if the TSTAT turns on the heater when AptTemp < hSP (the ELSE), then you only want it to turn off when AprTemp > hSP+Toffset. I believe your EMS prog will turn off the heater as soon as AptTemp> hSP. I see now the ELSEIF is meant to hold off heating while the space floats back down to hSP. What about when the heater is on while space is moving toward hSP+Toffset? The IF will turn it off at hSP.
Hi, Thanks for commenting I have no cooling system i just want to maintain a temp. of 22-26 inside the room. Your Help is Appreciated