How to set the starting temperature inside the zone and the range of comfortable temperatures in design builder

asked 8 years ago

updated 8 years ago

I want my Zone to start at 22c and heat until the zone temperature is 26c then the sys switches off until the zone temperature is 22 and so on

Preview: (hide)

1 Answer

Sort by » oldest newest most voted
3

answered 8 years ago

Ivan Korolija's avatar

Similar topic has been discussed here

Preview: (hide)
link

Comments

Thank you for answering but is there a way to do it directly with designbuilder without exporting to energyplus.

designbuilderknowledge's avatar designbuilderknowledge  ( 8 years ago )

if i try using the Ems file for my case Schedule:Constant,Cycle,OnOff,1; ! New schedule object

AvailabilityManager:Scheduled, ! Updated Availability Manager Packaged Rooftop Air Conditioner Availability Manager, Cycle; EnergyManagementSystem:Sensor, AptTemp, Thermal Zone 1, Zone Mean Air Temperature;

EnergyManagementSystem:Sensor, hSP, Thermal Zone 1, Zone Thermostat Heating Setpoint Temperature;

EnergyManagementSystem:Actuator, AvailSCH_Overwrite, Cycle, Schedule:Constant, Schedule Value; EnergyManagementSystem:ProgramCallingManager, Supervision,

designbuilderknowledge's avatar designbuilderknowledge  ( 8 years ago )

BeginTimestepBeforePredictor, HVAC_uncontolledloop_Supervision; EnergyManagementSystem:Program, HVAC_uncontolledloop_Supervision, SET Toffset = 1.00, IF AptTemp > (hSP - 0.01) && AptTemp < (hSP + 0.01), SET AvailSCH_Overwrite = 0, ELSEIF AvailSCH_Overwrite == 0 && AptTemp >= (hSP - Toffset) && AptTemp <= (hSP + Toffset), SET AvailSCH_Overwrite = 0, ELSE, SET AvailSCH_Overwrite = 1, ENDIF;

designbuilderknowledge's avatar designbuilderknowledge  ( 8 years ago )

I get severe errors and its not simulating

designbuilderknowledge's avatar designbuilderknowledge  ( 8 years ago )

I think DesignBuilder has EMS module (although in Beta version) link

Regarding the severe error I am not sure I can help just by seeing your code. You can switch on EMS outputs to check what your code does at each timestep.

Ivan Korolija's avatar Ivan Korolija  ( 8 years ago )