ASHRAE Loads in OpenStudio

asked 8 years ago

clguen's avatar

updated 8 years ago

Can Open Studio calculate ASHRAE loads?

Preview: (hide)

Comments

1

Which loads? Outdoor air? Plug loads? Lighting loads? Please be more specific in your question.

TaylorRoberts's avatar TaylorRoberts  ( 8 years ago )

1 Answer

Sort by » oldest newest most voted
5

answered 8 years ago

If your question is, can OpenStudio apply ASHRAE 90.1-20xx assumptions to a model, then the answer is yes. Take a look at this repo. The thing you probably want is the baseline automation measure, which hasn't been published to the building component library yet, but should be very soon.

Preview: (hide)
link

Comments

Does Open Studio use the ASHRAE Heat Balance Method to calculate design heating and cooling space loads (like IES preforms)?

clguen's avatar clguen  ( 8 years ago )
1

OpenStudio doesn't perform any physics calculations itself; it uses EnergyPlus for that. And, yes, EnergyPlus uses the heat balance method.

__AmirRoth__'s avatar __AmirRoth__  ( 8 years ago )

Yes, EnergyPlus is the engine and OpenStudio is the GUI. How do I view peak design heating and cooling space loads within the framework of OpenStudio?

clguen's avatar clguen  ( 8 years ago )

Look at the HVAC Sizing Summary table under EnergyPlus results.

__AmirRoth__'s avatar __AmirRoth__  ( 8 years ago )

The OpenStudio standard report also has peak load summary plots.

ljbrackney's avatar ljbrackney  ( 8 years ago )