Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
6

Modeling water-to-air heat pump with desuperheater for DHW

asked 2016-09-11 16:03:44 -0500

Only simple air-cooled DX objects are allowed to be input into theheating source object type field for the Coil:WaterHeating:Desuperheater object in EnergyPlus.

I need to model a water-to-air heat pump with a Desuperheater for DHW heating. Has anyone found a workaround for this in EnergyPlus?

I'm surprised the Coil:WaterHeating:Desuperheater object doesn't support more coil types like the HeatPump:WaterToWater:ParameterEstimation:Cooling or the Coil:Cooling:WaterToAirHeatPump:ParameterEstimation coil types.

If you also think this would be a nice feature, vote here: https://energyplus.uservoice.com/forums/258860-energyplus/suggestions/16019266-add-more-dx-systems-types-to-provide-waste-heat-fo

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2019-06-13 11:37:42 -0500

updated 2019-06-13 11:37:57 -0500

Hi, I am currently working on adding new choices for water heating desuperheater object. Look at this pull request for more details. Hopefully the next E+ release would at least cover the capability of modeling desuperheater with source type "Coil:Cooling:WaterToAirHeatPump:EquationFit"(so GSHP is available to combine) and "Coil:Cooling:DX:MultiSpeed". Besides, the tank type "WaterHeater:Stratified" would be also allowed.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2016-09-11 16:03:44 -0500

Seen: 568 times

Last updated: Jun 13 '19