Packaged Rooftop VAV w/Reheat Open Studio [closed]

asked 2016-08-31 11:47:40 -0600

jmoody's avatar

updated 2017-04-16 11:18:25 -0600

I can run my model with one rooftop defined with all thermal zones attached and it runs without any problems. When I break the thermal zones into two rooftop units I get an error. Anyone have experience with this?

image description

edit retag flag offensive reopen merge delete

Closed for the following reason question is not relevant or outdated by __AmirRoth__
close date 2017-04-16 11:18:55.391855

Comments

Can you post the error?

Adam Hilton's avatar Adam Hilton  ( 2016-08-31 14:42:41 -0600 )edit

That's not the error. Open up the *.err file and look for anywhere it says Fatal. Although, I'm going to preemptively assume it's because you have a water coil with a plant loop connection, but not air loop connection.

Adam Hilton's avatar Adam Hilton  ( 2016-08-31 23:42:08 -0600 )edit

That wasn't exactly the error but it was close. I had coils with a air loop connection but not a plant loop connection. Thanks for the help!

jmoody's avatar jmoody  ( 2016-09-01 11:13:49 -0600 )edit

Great! Glad you got it figured out.

Adam Hilton's avatar Adam Hilton  ( 2016-09-01 14:17:52 -0600 )edit