Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Low Temperature Radiant : Electric

asked 2016-08-23 06:05:20 -0500

khaled's avatar

updated 2017-05-08 18:34:27 -0500

How can i model ZoneHVAC:LowTempratureRadiant:Electric system for the floor of the house in energy plus?. i already tried to design it by using the example provided with the software but when i run the simulation the result is not changing. i am just changing the schedules and the parameters related with this template.

edit retag flag offensive close merge delete

Comments

You have not provided enough details to understand the issues that you facing.

JasonGlazer's avatar JasonGlazer  ( 2016-09-12 09:17:05 -0500 )edit

1 Answer

Sort by ยป oldest newest most voted
2

answered 2016-09-29 16:36:33 -0500

This was also posted to the helpdesk with idf file. The problem was missing ZoneHVAC:EquipmentConnections and ZoneHVAC:EquipmentList objects.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2016-08-23 06:05:20 -0500

Seen: 1,357 times

Last updated: Sep 29 '16