Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Is there a maximum air temperature in energyplus? How do I override it?

asked 2016-08-01 08:54:08 -0500

updated 2017-05-04 09:07:44 -0500

Running an Energy Plus model in witch air temperatures should be higher than 100°C I get several errors. Is there a upper bound for the air temperature in zones? Is it possible to override this maximum air temperature? It should reach at least 150°C.

edit retag flag offensive close merge delete

Comments

What exactly are you trying model that is so hot? A ceramics kiln?

__AmirRoth__'s avatar __AmirRoth__  ( 2016-08-01 09:03:50 -0500 )edit

@__AmirRoth__ I'm trying to model a Shadow box spandrel. It's insulated and it's exposed to the daylight. The model is described in this question: https://unmethours.com/question/19209...

milibr's avatar milibr  ( 2016-08-01 09:06:30 -0500 )edit

1 Answer

Sort by » oldest newest most voted
2

answered 2016-08-01 13:03:09 -0500

Archmage's avatar

I don't believe there are limits on the air temperatures but there are limits on the surfaces temperatures. Here the air is being heated by the surfaces so those are the limits that matter. The default surface temperature upper limit is 200C, but this can be changed on input using the HeatBalanceAlgorithm object's input field called Surface Temperature Upper Limit.

edit flag offensive delete link more