Variable water flow condenser loop

asked 8 years ago

ahespe's avatar

updated 8 years ago

Hi, does anyone know if it is possible to get variable flow pumping in your condenser water loop for heat rejection from a chiller? The example files provided with E+ that I have reviewed don't seem to allow this, only staged pumping. Cheers, Alex

Preview: (hide)

1 Answer

Sort by » oldest newest most voted
4

answered 8 years ago

Archmage's avatar

That is correct, the chiller models all have constant flow requests on the condenser side. The condenser loop flow can vary If there is more than one chiller staging on and off, but not if there is only one chiller.