Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Openstudio Air Inlet Node Name Missing

asked 2016-07-21 12:49:12 -0500

Palmiere's avatar

I am new to openstudio and i am trying to run a office building simulation to determine Cooling and Heating energy consume. I a model to test, i posted it at this link.

When i simulate it crashes with fatal error saying the following messages:

Severe * IP: IDF line~45517 Error detected in Object=COIL:COOLING:WATER, name=COIL COOLING WATER 2 * ~~~ ** Field [Air Outlet Node Name] is required but was blank

Severe * IP: IDF line~45543 Error detected in Object=COIL:COOLING:WATER, name=HW CHW FOUR PIPE INDUCTION TERMINAL CHW CLG COIL * ~~~ ** Field [Air Inlet Node Name] is required but was blank

I dont know exactly how to fix it.

Please could you give me a help looking at my model and showing me how to fix it?

Thank you.

Best Regards.

Sergio

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2016-07-22 15:22:58 -0500

You have four cooling coils and three heating coils attached to your chilled and hot water loops that are not being used by any terminal units. You should delete these coils. In the HVAC Systems tab, navigate to your loops and click the 'x' on the lower right of the coils to delete them:

image description

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2016-07-21 12:49:12 -0500

Seen: 914 times

Last updated: Jul 22 '16