asked 2014-12-10 11:29:19 -0600

Despina_pol's avatar

updated 2014-12-10 12:05:14 -0600

Hello,

I am using open studio 1.5 to model a multi-storey building which has split units in its rooms. I couldn't find a suitable HVAC system that matches split units. Can anyone help with that? Is it OK to insert a VRF system instead?

Thank you, Deapina.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
6

answered 2014-12-10 12:32:19 -0600

Are the split systems split AC units that have no heating? If you are you can use a PTAC and turn off the heating by setting the rated capacity and maximum water flow rate of the heating coil to zero.

Another option is to build an air loop with a "Unitary - Single Speed DX cooling - Cycling - Elec reheat" and turn off the electric reheat.

edit flag offensive delete link more

Comments

1

Another way to disable a coil is to create a schedule that is always off (0) and assign it to the coil availability schedule. I've used this successfully on the heating coil of cooling only FCUs.

MatthewSteen's avatar MatthewSteen  ( 2014-12-10 12:57:49 -0600 )edit

This question might be a duplicate with https://unmethours.com/question/1814/...

Kyle Benne's avatar Kyle Benne  ( 2014-12-14 20:42:18 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2014-12-10 11:29:19 -0600

Seen: 1,030 times

Last updated: Dec 10 '14