Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

OpenStudio error in Four Pipe Induction ATU: Induced Air Inlet Node Name is blank

asked 2016-07-19 04:03:43 -0500

Chris's avatar

updated 2018-08-25 18:29:09 -0500

I'm up against a recurring error very similar to the one described here.

The issue is a blank field for the Induced Air input field of a Four Pipe Induction Terminal supplied by Air Handling Unit 1. The interesting thing here is that every time I add a new terminal unit in a new zone the error seems to move to another (the new) terminal unit.

** Severe  ** IP: IDF line~7462 Error detected in Object=AIRTERMINAL:SINGLEDUCT:CONSTANTVOLUME:FOURPIPEINDUCTION, name=THB.08
**   ~~~   ** Field [Induced Air Inlet Node Name] is required but was blank

*************   7457   THB.08,                                 !- Name
*************   7458   ,                                       !- Availability Schedule Name
*************   7459   0.48,                                   !- Maximum Total Air Flow Rate {m3/s}
*************   7460   2.5,                                    !- Induction Ratio
*************   7461   Node 622,                               !- Supply Air Inlet Node Name
*************   7462   ,                                       !- Induced Air Inlet Node Name

I tried changing the type of analysis to detailed analysis as mentioned here, but that didn't make any difference.

In addition, the simulation ran before, but once I added additional ZoneExhaust and Ventilation:DesignFlowRate objects it started failing, maybe that has something to do with it.

Here is a link to the OpenStudio file.

image description

edit retag flag offensive close merge delete

Comments

Please refrain from creating new tags (blank-field in this case)

Julien Marrec's avatar Julien Marrec  ( 2016-07-19 04:39:53 -0500 )edit

1 Answer

Sort by ยป oldest newest most voted
2

answered 2016-07-19 05:09:31 -0500

updated 2016-07-19 05:12:10 -0500

This is definitely an OpenStudio problem, you should open an issue on Github

My two cents:

  • You have correctly identified that when you add a new one, the problem seems to move around. Well, partially. If you click on the splitter, and add a new zone, behind the scene the last ATU (Let's call it ATU-1) seems to be cloned to add this new thermal zone with a new ATU (let's call it ATU-1bis), and something seems amiss in the sense that the it reset the inducedAirInletNode of this ATU-1.
  • If you're looking for a quick work around, drop the thermal zone first, then add a Four Pipe Induction ATU to the inlet node of the zone. This works fine (the addToNode method works)
  • The initial design choice is questionable to me. It seems that the induced air inlet node is set during the call to the addToNode method (see source code here). I think it would make more sense to set the inducedAirInletNode during the forward translation, and to completely hide the inducedAirInletNode property in the API as well (it's not visible in the OS App but there's a getter (no setter) in the API).
edit flag offensive delete link more

Comments

Added a Github issue here

Julien Marrec's avatar Julien Marrec  ( 2016-07-19 05:10:45 -0500 )edit

Side note: you still have many interzone surfaces that aren't matched correctly. And good luck with the E+ simulation runtime, it's gonna hurt.

Julien Marrec's avatar Julien Marrec  ( 2016-07-19 05:15:17 -0500 )edit

Brilliant, this allowed me side-step the problem and add the unit without any difficulties. Thanks Julien, also for submitting the issue as well.

Chris's avatar Chris  ( 2016-07-19 05:58:07 -0500 )edit
1

@Chris FYI, I just fixed this in PR #2887. Not sure when that's going to be integrated though.

Julien Marrec's avatar Julien Marrec  ( 2017-12-05 08:02:49 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2016-07-19 04:03:43 -0500

Seen: 279 times

Last updated: Jul 19 '16