Can We Connect One AirLoop with Another AirLoop

asked 8 years ago

lyw0211's avatar

updated 8 years ago

I would like to use EnergyPlus or OpenStudio to model a huge AHU system that supply the cooled air to each floor by using super fans. And each floor also has some terminal boxes that can modulate and heat the cooled air before delivering to the zone. So my idea is as following:

1) Create a central air loop for that huge AHU system 2) Create an extra air loop for each floor that contains the zone and terminal box. 3) Connect each floor's air loop to the central air loop to allow the cooled air to each floor.

Does anyone has the similar experience in connecting two air loops together by some methods? If my ideas can't be true, does anyone has a better idea? Thanks!

Preview: (hide)

1 Answer

Sort by » oldest newest most voted
4

answered 8 years ago

Archmage's avatar

No, this is not going to work in current EnergyPlus. There is development work going on to add a feature for central outdoor air system serving multiple airloops, but that will be for a future release (https://energyplus.uservoice.com/foru...).

At this point you could do either one single huge airloop, if all the floors are running similarly, or one airloop per floor, if there are some big difference in the individual floor AHU operating conditions.

Preview: (hide)
link

Comments

@Archmage, Thank you! This is very helpful!