Questions about chiller performance curves and chiller setting.
Hi everyone, here are my specification of chillers that I simulate in EnergyPlus,
I choose Chiller:Electric:EIR
as build of CHU-1~2.
But I only can choose Chiller:Electric:Reformulated EIR
as build of BHU-1~2, because of my evaporator fliud temperatue is below 0℃.When I use Chiller:Electric
and Chiller:Electric:EIR
to simulate BHU-1~2 it will show error about my evaprator fluid temperature.
Can anyone tell me why? That's my first question.
My second question is about chiller performance curves.
From documentation [EngineeringReference], the topic of Electric ChillerModel Based on Condenser Entering Temperature says there are three curves to determine chiller operation at off-reference conditions.
1) Cooling Capacity Function of Temperature Curve
2) Energy Input to Cooling Output Ratio Function of Temperature Curve
3) Energy Input to Cooling Output Ratio Function of Part Load Ratio Curve
The equation of curve 1 and 2 are same, how come the coefficients are different?
(From DataSet\Chillers.idf
)
It also showed in Commercial Buildings Energy Modeling Guidelines & Procedures (MGP) chapter 6.8.2 CHILLERS link text
I have the same question about different coefficients problem in Electric ChillerModel Based on Condenser Leaving Temperature in [EngineeringReference].
If there is any response, then I would be very grateful.
Sincerely, Yueh-Chin
For your first question, can you post the error you're seeing? Are you creating a user defined fluid and setting that as the working fluid for the loop? I suspect that you aren't and the error is because you're freezing the water. The change from
...:EIR
to...:ReformulatedEIR
is just whether the performance is based off the entering or leaving condenser fluid temperature.I may forgot to change fluid type when I simulate last time, I will go check again, thanks to your answer!