Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
4

modeling a cooling coil water inlet node

asked 2014-12-05 16:58:14 -0500

E Boxer's avatar

updated 2017-02-17 07:58:25 -0500

image description

The image above shows the components needed to model a Controller:WaterCoil. I am doing this for the purpose of Dehumidification control on a system of type AirLoopHVAC:UnitarySystem. I happen to be using a coil of type Coil:Cooling:DX:TwoStageWithHumidityControlMode.

In theory, the Controller:WaterCoil is supposed to talk to the Humidity and Temperature Setpoint managers for a zone and adjust the amount of cold water in the coil. However, I cannot find actuator node description in the model. In fact, I don't see any cooling coil water inlet nodes in the model. This is required input for the Controller:WaterCoil "Actuator Node Name".

Is it a problem to use the IDF editor in doing this? Does and actuator need to be created? (I've tried this)

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
5

answered 2014-12-10 09:12:55 -0500

updated 2017-02-17 07:58:14 -0500

I am not sure what modelling software you are using but the actuator node is the node on your cooling coil that you want to vary to meet the criteria you have set. So for instance, if you want an air humidity of 8g/kg and an air temperature of 15°C coming off your coil, your sensor node for those criteria is the air node coming out of the cooling coil and the actuator node is the water node going into the coil, the water entering the coil needs to vary in flow and temperature for the air to meet the criteria.

This is the case for a water coil, however, if you have a DX coil you do not need a Controller:WaterCoil. The system will know itself to look into the correct places. You will need setpoints and to put the right type of control in your DX system.

edit flag offensive delete link more

Comments

Annie, Thanks for this insight about DX coil control in EnergyPlus! This approach of controlling the coil directly, with EMS code, and a zone humidistat worked out.

E Boxer's avatar E Boxer  ( 2014-12-10 10:58:17 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2014-12-05 16:58:14 -0500

Seen: 517 times

Last updated: Feb 17 '17