Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Modelling mechanical ventilation without air handling unit

asked 2016-06-06 09:15:16 -0500

Verla's avatar

What is the best way to model mechanical ventilation without any air conditioning system, meaning it is only with fan and duct-work serving multiple zones. Can I use ZoneMixing model? Or AirflowNetwork?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2016-06-06 10:09:29 -0500

Archmage's avatar

ZoneVentilation:DesignFlowRate is intended for this.

edit flag offensive delete link more

Comments

Thanks. I have started implementing your suggestion. If I want to consider the air flow pattern, how can I input the information of air paths, using the Node-Branch Management?

Verla's avatar Verla  ( 2016-06-07 03:41:31 -0500 )edit

If you mean the air flow pattern within the zone then there are some roomair models to help with this depending on the diffuser setup you have. But those models are not really connected to ZoneVentilation:DesignFlowRate (because fan powered mechanical ventilation is usually mixing the room's air). If you want to do roomair modeling you would use AirflowNetwork, or an air handling unit, and not the simple mechanical ventilation.

If you just mean how to duct the air into the zone, you don't need to do anything else besides have a ZoneVentilation:DesignFlowRate for each zone.

Archmage's avatar Archmage  ( 2016-06-07 07:59:48 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2016-06-06 09:15:16 -0500

Seen: 100 times

Last updated: Jun 06 '16