Error detected in Object=SETPOINTMANAGER:SINGLEZONE:REHEAT

asked 2016-06-04 15:28:17 -0600

when I try to run my simulation it shows this error:

  • Severe * IP: IDF line~7378 Error detected in Object=SETPOINTMANAGER:SINGLEZONE:REHEAT, name=SETPOINT MANAGER SINGLE ZONE REHEAT 2 * ~~~ * Field [Control Zone Name] is required but was blank...

image description

I am sure that it is due to " Packaged Rooftop Air Conditioner 7" and it should be "Packaged Rooftop Air Conditioner 1" but I do not know how to do that? My file is here to download.

Thanks in advance for any guidance.

edit retag flag offensive close merge delete

2 Answers

Sort by ยป oldest newest most voted
2

answered 2016-06-04 16:25:50 -0600

The error message means your airloop is not controlling any zones. Go back the HVAC tab and go through each airloop for insanity check.

edit flag offensive delete link more
1

answered 2016-06-05 05:20:02 -0600

updated 2016-06-05 05:21:01 -0600

@Yijia Wang,Thank you so much. As you said I checked my air loop "Packaged Rooftop Air Conditioner 1" and understood there was not zone of classroom-2, then I applied this zone for it and also I added a Diffuser from Libray(Air Terminal Single Duct Uncontrolled).Now my model works.

image description

image description

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2016-06-04 15:28:17 -0600

Seen: 734 times

Last updated: Jun 05 '16