Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

Heating/cooling sizing factor when using ideal air loads in Open Studio?

asked 2016-06-03 04:36:02 -0600

DavidFGG's avatar

updated 2017-05-08 15:43:59 -0600

I am using ideal air loads in my model. When i changed the heating sizing factor and cooling sizing factor to 1.00, the results for heating and cooling energy did not change (End Uses).

Does this mean that no system energy losses are taken into account for the heating and cooling system when using ideal air loads ?

Because in the end results the total site and net site energy are equal (also total an net source energy).

edit retag flag offensive close merge delete

Comments

1

Please do not include greetings like "thx in advance" per our convention (see here).

Also, tags should be used when they are appropriate: unless you're actually talking about something in sketchup, don't include this tag. But do include existing tags that are appropriate such as hvac-sizing and ideal-loads-air-system

Julien Marrec's avatar Julien Marrec  ( 2016-06-03 05:18:31 -0600 )edit
1

OK, i will answer and tag my questions appropriately from now on.

DavidFGG's avatar DavidFGG  ( 2016-06-03 11:15:02 -0600 )edit

1 Answer

Sort by ยป oldest newest most voted
3

answered 2016-06-03 05:21:25 -0600

updated 2016-06-03 08:19:51 -0600

As the name implies, Ideal Loads Air System is ideal. Refer to the Input/Reference guide for more information: ZoneHVAC:IdealLoadsAirSystem

This component can be thought of as an ideal unit that mixes air at the zone exhaust condition with the specified amount of outdoor air and then adds or removes heat and moisture at 100% efficiency in order to produce a supply air stream at the specified conditions. The energy required to condition the supply air is metered and reported as DistrictHeating and DistrictCooling.

edit flag offensive delete link more

Comments

OK, that is why the total site and net site energy are the same. Tnx

DavidFGG's avatar DavidFGG  ( 2016-06-03 11:33:13 -0600 )edit
1

@DavidFGG , No it is bacause you do not have renewable systems in your model

Ag's avatar Ag  ( 2020-10-01 05:33:26 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2016-06-03 04:36:02 -0600

Seen: 920 times

Last updated: Jun 03 '16