Is it possible to somehow adjust the conditioned floor area in OpenStudio?

By default the conditioned floor area equals the total floor area.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2016-06-03 04:15:19 -0600

updated 2016-06-03 04:23:35 -0600

Don't add any HVAC system serving the zone.

See the DetermineBuildingFloorArea in OutputReportTabular.cc:

if ( Zone( iZone ).isPartOfTotalArea ) {
        buildingGrossFloorArea += curZoneArea;
        // If a ZoneHVAC:EquipmentConnections is used for a zone then
        // it is considered conditioned. Also ZONE SUPPLY PLENUM and ZONE RETURN PLENUM are
        // also is considered conditioned.
        if ( Zone( iZone ).SystemZoneNodeNumber > 0 ) {
            buildingConditionedFloorArea += curZoneArea;
        }
    }
edit flag offensive delete link more

Comments

I think you're using IdealLoads given your other question. Just don't enable ideal loads for these zones too.

Julien Marrec's avatar Julien Marrec  ( 2016-06-03 04:24:37 -0600 )edit