Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

OpenStudio 1.11 not importing valid IDF file EP 8.5

asked 2016-06-02 06:24:00 -0500

updated 2020-03-08 11:32:38 -0500

When importing an idf file, OpenStudio complains that the idf file is not valid:

image description

Although airloops and plantloops are not imported anyway (including e.g. WaterHeater:HeatPump:PumpedCondenser objects), it complains about an invalid numerical field in a plant loop component, and stops importing.

Is this a bug, and what is the remedy ?

edit retag flag offensive close merge delete

Comments

In general, OpenStudio does not import IDF HVAC.

__AmirRoth__'s avatar __AmirRoth__  ( 2016-06-02 11:40:02 -0500 )edit

1 Answer

Sort by ยป oldest newest most voted
0

answered 2016-06-03 01:42:07 -0500

Since OpenStudio generally does not import IDF HVAC, any syntax checks by the Importer on HVAC components could be considered unnecessary from the software developer's perspective.

For OpenStudio users, there is of course a trivial work-around, i.e. delete the object(s) which Openstudio Importer complains about, or correct specific input parameters of such objects.

In the above example, the air-to-water heatpump minimum temperature for operation was set to below zero degrees Celsius (along with an IDD file modification to allow this in EnergyPlus), which apparently was still illegal for OpenStudio. But after changeing the minimum temperature input, the OpenStudio import was successful.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2016-06-02 06:24:00 -0500

Seen: 175 times

Last updated: Jun 03 '16