How to model service hot water for midrise apartments

asked 2016-05-31 12:42:20 -0500

Morteza's avatar

What is the best way to model Service Hot Water for a MidriseApartment in OpenStudio? Assuming each apartment unit has its own water heater, is it more appropriate to select separate water use connections and water use equipments for each of the apartment units, which is very time consuming, or is it okay to select a water use connection for a group of the apartment units located in each floor or in the whole building?

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
2

answered 2016-06-01 01:17:29 -0500

updated 2016-06-01 01:29:40 -0500

Adding a new plant loop with a water heater and a water use connection for each apartment would be a very easy task using a measure. But you'll get dinged on simulation time if you end up with 150 plant loops. Here is some pseudo code if that's helpful: Loop on all spaces, check if the spaceType corresponds to appartment, if so create a plant loop with the necessary components (water use connection and equipment, water heater, pump, setpoint manager). You can also get the spaceType you need and call spaceType.spaces...

Note that all of that can de done using or adapting some of the work done as part of openstudio-standards. See Prototype.HVAC_Systems.add_swh_loop and Prototype.HVAC_Systems.add_swh_end_uses especially.

I guess the true question is what do you know about the efficiency of the water heaters in each space? Are they modulating? Is it a tank-style water heater that just turns on and off? If natural gas, do you have an automatic damper to close the flue when the water heater is off (are standby losses a big factor?) Is water heating usage a big driver in your building? How well do you think you know the actual hot water draw versus various losses?

The answer to these questions will determine whether it's an appropriate assumption to model it as a single water heater or if it would be too crude of an assumption.

edit flag offensive delete link more

Comments

(I realize this is in the gray area between a comment and an actual answer)

Julien Marrec's avatar Julien Marrec  ( 2016-06-01 01:18:31 -0500 )edit

@Julien, thank you very much for the helpful information, I will study these options carefully. However, I did not find any measure for service water heater in BCL library, could you please provide a link to this measure? In addition, this is a LEED project and the baseline model should be consistent with ASHRAE 90.1-2007 modeling protocol, hence I have to provide answer to the entire question that you mentioned from the standard for the baseline model, is this correct? Thanks again for all your help!

Morteza's avatar Morteza  ( 2016-06-01 11:04:11 -0500 )edit

If there's no mesure in BCL you have to create it. It'll be a simple mesure though.

Not sure I understand what's your actual question about the LEED and ASHRAE protocol

Julien Marrec's avatar Julien Marrec  ( 2016-06-02 05:25:11 -0500 )edit

Julien, thank you for your response. I am not quite familiar with creating measures, so thought using following procedure to model SHW for the apartment units of the model: 1. Create a new plant loop with a water heater and water use connections 2. Select an unconditioned space in the underground parking garage that is not part of the building total floor area 3. Select a multiplier equal to the number of apartment units within the building for the Thermal Zone of the selected space. 4. Select this space as “Space Name” for each of the Water Use Equipments Is this procedure correct?

Morteza's avatar Morteza  ( 2016-06-03 17:56:57 -0500 )edit

You actually don''t have to specify a space name in the water use equipment. This is optional, to account for heat gains (latent).

This would work if you only care about getting hot water heating consumption in your model, but keep in mind it's a simplification

Julien Marrec's avatar Julien Marrec  ( 2016-06-04 03:36:59 -0500 )edit

Julien, thank you for the confirmation and additional information, the only purpose of selecting a space name for the water use equipment was to use multiplier (total number of the residential units), is there other way(s) to select multiplier for water use equipment?

Morteza's avatar Morteza  ( 2016-06-04 11:30:33 -0500 )edit

just play with the GPM. For example I usually end up with something like 20 GPM with a schedule to model DHW consumption of an entire multifamily building.

Julien Marrec's avatar Julien Marrec  ( 2016-06-05 15:27:13 -0500 )edit

Thank you very much for your help, your guidance solved my problem. I revised the peak flow rates of the fixtures in Loads tab per total building flow and simulation results showed the expected values.

Morteza's avatar Morteza  ( 2016-06-08 16:23:07 -0500 )edit

I still need some advice on this subject. When you set the Max Loop flow rate to 20 GPM and run the model what was the percentage of annual SHW energy consumption compared to the whole building annual energy consumption? In my model, the Max Loop Flow Rate is 47.137 gpm and annual energy consumption of SHW is only 2% of the annual energy consumption of the building, which is not realistic. With the same fixture definitions: lavatory faucet 2.2 gpm, shower 2.5 gpm and kitchen sink 2.5 gpm I changed the Max Loop Flow Rate to Autosized, but this did not change the simulation results.

Morteza's avatar Morteza  ( 2016-06-11 16:13:08 -0500 )edit

Max loop flow rate doesn't have to be set. I usually use one water use connection with one linked water use equipment definition where I set a flow rate and a schedule multiplier. Based on that, you should be able to calculate the water heating consumption you expect and make sure it matches more or less. One thing to beware is whether your consumption will be categorized as water heating by E+ or not (if you use a waterheater:mixed it will, if it's a boiler (via a HX or not) it probably won't).

Julien Marrec's avatar Julien Marrec  ( 2016-06-13 02:12:24 -0500 )edit
1

Thank you very much for your response. This process works, I can get the expected energy consumption related to SHW.

Morteza's avatar Morteza  ( 2016-06-13 17:52:41 -0500 )edit