Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Pump setpoint manager

asked 2016-05-28 08:02:24 -0500

Hamid's avatar

updated 2016-05-29 09:28:38 -0500

Hello, I'm modeling a plant in which a constant-speed circulation pump in the condenser loop must be on/off according to the zone air source heat pump on/off profile. Is there any set point-manager which is appropriate for that? Thank you so much.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2016-05-28 12:55:24 -0500

If you set the 'Pump Control Type' field to 'Intermittent', the pump should only run when there is demand from the coils attached to the demand side of the loop. When the heat pump coils are scheduled off, there should be no demand and therefore no flow.

edit flag offensive delete link more

Comments

Thank you so much.

Hamid's avatar Hamid  ( 2016-06-05 13:57:51 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2016-05-28 08:02:24 -0500

Seen: 222 times

Last updated: May 28 '16