Openstudio doesn't calculate Design load with sizing factor [closed]

asked 2016-05-27 09:07:31 -0600

dana94_08's avatar

updated 2020-03-07 22:03:58 -0600

Hi I have a problem, Openstudio doesn't calculate Design load with sizing factor when I only use a thermostat for cooling. In my country we never use heating systems, so I don´t need to calculate the design load for heating. Thank you

edit retag flag offensive reopen merge delete

Closed for the following reason the question is answered, right answer was accepted by dana94_08
close date 2016-06-17 18:04:13.912795

Comments

See if this post helps. It describes how to use ThermostatSetpointDualSetpoint when you want a cooling only system.

David Goldwasser's avatar David Goldwasser  ( 2016-05-27 09:49:56 -0600 )edit

What I did understand is that I have to put a heating schedule and it has to be with a lower temperature than my cooling schedule. So if I put a temperature of 12°C for the heating schedule there will be no mistake?

dana94_08's avatar dana94_08  ( 2016-05-27 10:35:25 -0600 )edit

Yes, in addition to being lower than your cooling schedule, you may want it lower than any temperatures the building will see, so it doesn't show up as hours heating setpoint not met.

David Goldwasser's avatar David Goldwasser  ( 2016-05-27 10:50:01 -0600 )edit