Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Is there a simple way to get a report of the outdoor air volume through openstudio

asked 2016-05-26 21:51:52 -0500

shahin1992's avatar

updated 2016-05-27 02:09:30 -0500

I'm a beginner to openstudio and I'm looking for a simple and effective way to get the zone outdoor air volume flow rate and I'm not familiar with getting data from Energyplus directly. I wonder what is the best variable to get that given that I tried the variable Zone Mechanical Ventilation Mass Flow Rate shown in the picture and got no output.

image description

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2016-05-27 02:46:39 -0500

You want Zone Mechanical Ventilation Current Density Volume. Note that this only reports the outside air that's delivered Mechanically as the name implies.

You might want Zone Infiltration Current Density Volume as well.

Output:Variable,*,Zone Mechanical Ventilation Current Density Volume,hourly; !- HVAC Sum [m3]
Output:Variable,*,Zone Infiltration Current Density Volume,hourly; !- HVAC Sum [m3]
edit flag offensive delete link more

Comments

thanks very much for your reply

shahin1992's avatar shahin1992  ( 2016-05-30 07:52:05 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

2 followers

Stats

Asked: 2016-05-26 21:51:52 -0500

Seen: 234 times

Last updated: May 27 '16