Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Photovoltaic's in EnergyPlus output power above rated level

asked 2016-05-18 12:21:48 -0500

Alex Bennett's avatar

I am modelling photovoltaic's in EnergyPlus based off of the Example File 'ShopWithPVandStorage.idf'. In the component ElectricLoadCenter:Generators you set a 'Generator Rated Electric Power Output' which I assumed would be the max output the generator could produce. But when I set this value to 0 there was still photovoltaic energy production even though I had rated the power output to 0 W. This leads me to guess that there is some fixed value EnergyPlus is assuming for the output since I also tested with 1000 W and 2000 W and three cases(including 0 W) resulted in the same energy production. Is there another spot I need to set the generator power output?

edit retag flag offensive close merge delete

Comments

That Generator Rated Electric Power Output field does very little for PV, but it does get used in a LEED table summary report for the size of the PV. EnergyPlus is modeling the PV production based on a whole lot of factors, it is not assuming some fixed output.

Archmage's avatar Archmage  ( 2016-05-20 08:20:59 -0500 )edit

1 Answer

Sort by ยป oldest newest most voted
2

answered 2016-05-18 18:00:29 -0500

updated 2016-05-18 18:02:55 -0500

I think this will help. Basically, you control the rated wattage by surface area and cell efficiency. Most panel power ratings are given at STC conditions with 1000 $W/m^{2}$ incident radiation . So as an example, if you specify a 100 $m^{2}$ system with 15% cell efficiency, that corresponds roughly to a 15 kW system.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2016-05-18 12:21:48 -0500

Seen: 215 times

Last updated: May 18 '16