Ventilation system with scheduled air flow rate?

asked 2016-05-11 08:33:58 -0600

aleph's avatar

updated 2017-05-04 09:08:43 -0600

I need to model a ventilation system where I control with schedules BOTH the total air flow rate AND the air temperature, regardless of the heating/cooling needs of the zones. Is this possible? I have tried but I have found only the way to control the outdoor air flow rate, while I need to set the total air flow rate (outdoor+recycled). The outdoor air fraction is not an important variable in my case.

What I need to model is a pure ventilation system, but E+ always tends to use it as a cooling system and then override any air flow rate controller that I tried.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2016-05-12 23:11:03 -0600

Chandan Sharma's avatar

ZoneHVAC:OutdoorAirUnit with unit control type as TemperatureControl may serve the purpose here.

edit flag offensive delete link more