Unitary system and OA system economizer does not leads to reduced cooling power
I 'm trying to model a CRAC of a small Data Center and as you can see in the image its a Unitary system and OA system
I followed "The third edition of ASHRAE’s Thermal Guidelines for Data Processing Environments"
but the operation of the economizer does not leads to reduced cooling power rate. It has to do with the settings or has to do with the geographical location and the local climatic conditions (humidity, enthalpy etc.)?
Here 's my model:
Thanks in advance !!!
As a first step you can report out the
Output:Variable
calledAir System Outdoor Air Economizer Status
and check if the economizer is actually being activated as expected.@aparker Thanks for your comment. Reporting out the Air System Outdoor Air Economizer Status I see that economizers operation depends on climate conditions. The only time that operates when the dry bulb temperature is above 18 C. The recommended envelope is very restricted. I 'll consider wider envelopes. Thanks!