Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
4

Calculated Design Cooling load is Zero [closed]

asked 2016-05-09 05:24:21 -0500

FSilenzi's avatar

updated 2016-05-09 07:31:39 -0500

I am finding this error in the simulation error referred to some of my thermal zones.

I have checked here and here: I looked at all of my thermostats (which are fine) and I do not have any cooling cabinet in my model. I used also the procedure illustrated here to assure the ACH for every zone are mantained. The errors I get are

   ** Warning ** Calculated design cooling load for zone=THERMAL ZONE: F2-OR 2 is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design cooling load for zone=THERMAL ZONE: F2-OR 3 is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design cooling load for zone=THERMAL ZONE: F2-OR 4 is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design cooling load for zone=THERMAL ZONE: F2-OR1 is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design cooling load for zone=THERMAL ZONE: F4-TRASPLANT OR is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design cooling load for zone=THERMAL ZONE: F6-CARDIAC OR is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design cooling load for zone=THERMAL ZONE: SF1-ANGIOGRAPHY is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design cooling load for zone=THERMAL ZONE: SF1-TAC is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design cooling load for zone=THERMAL ZONE: SF2-DRESSING ROOM is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** ManageSizing: For a plant sizing run, there must be at least 1 Sizing:Plant object input. SimulationControl Plant Sizing option ignored.

What can cause this kind of warining? Shall I ignore them since the simulation runs? I do not think it would be great to ingore them since they are sizing-error-related warnings.

edit retag flag offensive reopen merge delete

Closed for the following reason question is not relevant or outdated by FSilenzi
close date 2016-05-16 07:24:42.443240

1 Answer

Sort by ยป oldest newest most voted
2

answered 2016-05-09 15:35:17 -0500

Determinant's avatar

updated 2016-05-09 15:37:25 -0500

Verify that the people, light, equipment schedules are not 0 for the hours for the design runs. This was mentioned in one of the articles you referenced but not specifically verified yet by you.

edit flag offensive delete link more

Careers

Question Tools

2 followers

Stats

Asked: 2016-05-09 05:24:21 -0500

Seen: 1,205 times

Last updated: May 09 '16