Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
4

Calculated Design Cooling load is Zero [closed]

asked 8 years ago

FSilenzi's avatar

updated 8 years ago

I am finding this error in the simulation error referred to some of my thermal zones.

I have checked here and here: I looked at all of my thermostats (which are fine) and I do not have any cooling cabinet in my model. I used also the procedure illustrated here to assure the ACH for every zone are mantained. The errors I get are

   ** Warning ** Calculated design cooling load for zone=THERMAL ZONE: F2-OR 2 is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design cooling load for zone=THERMAL ZONE: F2-OR 3 is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design cooling load for zone=THERMAL ZONE: F2-OR 4 is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design cooling load for zone=THERMAL ZONE: F2-OR1 is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design cooling load for zone=THERMAL ZONE: F4-TRASPLANT OR is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design cooling load for zone=THERMAL ZONE: F6-CARDIAC OR is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design cooling load for zone=THERMAL ZONE: SF1-ANGIOGRAPHY is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design cooling load for zone=THERMAL ZONE: SF1-TAC is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design cooling load for zone=THERMAL ZONE: SF2-DRESSING ROOM is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** ManageSizing: For a plant sizing run, there must be at least 1 Sizing:Plant object input. SimulationControl Plant Sizing option ignored.

What can cause this kind of warining? Shall I ignore them since the simulation runs? I do not think it would be great to ingore them since they are sizing-error-related warnings.

Preview: (hide)

Closed for the following reason question is not relevant or outdated by FSilenzi
close date 2016-05-16 07:24:42.443240

1 Answer

Sort by » oldest newest most voted
2

answered 8 years ago

Determinant's avatar

updated 8 years ago

Verify that the people, light, equipment schedules are not 0 for the hours for the design runs. This was mentioned in one of the articles you referenced but not specifically verified yet by you.