OpenStudio Results - Exterior Lighting correct?

asked 9 years ago

Matt Koch's avatar

updated 9 years ago

Hi,

I am using the Exterior Equipment in the Facility Tab to specify exterior lighting at 6,698 W. It is running 12 hours a day 365 days a year so uses approximately 2,444.8 kWh/month or 29,337.2 kWh/y. Yet, OpenStudio Results Exterior Lighting is reporting this as 29.34 kWh (presumably per year - there really should be an "Annual" annotation if that is so). Am I misinterpreting this number - is it referring to some period other than a year?

Thanks,

Matt

Preview: (hide)

Comments

Note that the annual exterior lighting consumption can also be found in the OpenStudio report under Monthly Overview and then expanding the "Electricity Consumption (kWh) - view table". Exterior Lighting will be a row in that table with an annual (as well as monthly) values.

shorowit's avatar shorowit  ( 8 years ago )

1 Answer

Sort by » oldest newest most voted
3

answered 9 years ago

updated 9 years ago

The OpenStudio Results are produced by a measure that gets values from the EnergyPlus results, so check the Lighting Summary report there for the real values.

It looks like the measure is incorrectly doing a conversion here, which may be happening if you're converting the results to IP units.

FYI @David Goldwasser

Preview: (hide)
link

Comments

Good catch, I'll fix both the unit conversion and extend the label to specify consumption as annual. https://github.com/NREL/OpenStudio/is...

David Goldwasser's avatar David Goldwasser  ( 9 years ago )