Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

How to describe a opening between two zones in SU with legacy open studio

asked 2016-04-27 23:11:10 -0500

gaofeng's avatar

updated 2021-07-11 16:11:09 -0500

Sometimes, there is no internal wall between two zones, but just a opening. So, how to describe this are in SU with legacy open studio. Though I can draw this situation in SU software, I'm not sure whether this method accord with the principle of software

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2016-06-15 17:20:36 -0500

Adam Hilton's avatar

If they are two different spaces that you plan to put on two different thermal zones you can use an air wall construction for the opening and add a ZoneCrossMixing object for each thermal zone.

If they are two different spaces that you plan to put on the same thermal zone, the opening is extraneous.

edit flag offensive delete link more

Comments

1

For Legacy specific answer just skip the part about the air wall construction. That is unique to the OpenStudio Model format, and only affects Radiance, not EnergyPlus. Also the ZoneCrossMixing won't be exposed in the legacy plugin, so you will need to add that to the IDF file externally.

David Goldwasser's avatar David Goldwasser  ( 2016-06-15 18:51:24 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2016-04-27 23:11:10 -0500

Seen: 130 times

Last updated: Jun 15 '16