2

Ideal Loads and Economizer set up [closed]

asked 2016-04-27 03:59:45 -0600

FSilenzi's avatar

updated 2017-10-18 07:20:27 -0600

I need to run simulations in which the cooling and heating loads are supplied via Ideal Loads. I have opened another question here which I have followed, but working on the model have brought other questions to my mind. I have used the "ideal loads" option to model the air conditioning system, setting the ACH as indicated to me in the previous question, the simulation ran and I compared these variables:

-Zone Ideal Loads Zone Sensible Cooling Rate

-Zone Ideal Loads Supply Air Sensible Cooling Rate

which are exactly equal. As far as I know, there should be a difference between the two variables if the system is supplying unconditioned outdoor air whenever the outdoor air temperature is suitable in order to save energy.

I am then asking you, how can I understand if the OA is supplied (using OpenStudio) and what option/parameters shall I check in order to model the system correctly?

Thanks

edit retag flag offensive reopen merge delete

Closed for the following reason question is not relevant or outdated by FSilenzi
close date 2016-06-10 02:42:13.545516

1 Answer

Sort by ยป oldest newest most voted
2

answered 2016-04-27 10:36:35 -0600

Adam Hilton's avatar

Like for the ...Supply Air... and the ...Zone... output variables there are also a set of ...Outdoor Air... output variables for the ideal air loads system. You can use that to check the energy/rates for outdoor air.

OS leaves all the parameters in the IdealLoadsAirSystem object to defaults, and I don't believe you can change anything in the GUI, so you'll have to write a measure. The default for the outdoor air parameter is to not have any outdoor air which would explain the lack of difference you're seeing.

edit flag offensive delete link more

Comments

Thanks @adhilton If such a measure would exist I shall find it on the BCL right? Or is there another repository/library which I can check?

FSilenzi's avatar FSilenzi  ( 2016-04-28 01:42:07 -0600 )edit

I managed to input the correct objects for Ideal Loads in E+ idf editor, and the simulation seems to run seamlessly. I have temperature match as well as hourly air changes satisfy the requirements. What still confuses me is how can I check if the enconomizer is working, because I have Zone Ideal Loads Economizer Active Time as output, as well as Zone Ideal Loads Supply Air Sensible Heating Rate (a) and Zone Ideal Loads Zone Sensible Heating Rate (b). I have a different from b even if the economizer has 0 hours of functioning. Why this could happen?

FSilenzi's avatar FSilenzi  ( 2016-05-02 03:07:43 -0600 )edit

You could have a heating limit set or a specified minimum of outdoor air being brought in. Other than that, not really sure.

Adam Hilton's avatar Adam Hilton  ( 2016-05-02 08:40:51 -0600 )edit

ZoneHVACIdealLoadAirSystem has "heating limit" set to "no limit". The only limits I have set are for cooling because I could not turn on the economizer without setting "cooling limit" as "limit flow rate" and the "maximum cooling rate flow rate" set to autosize.

FSilenzi's avatar FSilenzi  ( 2016-05-02 09:45:31 -0600 )edit