Radiant flow system with heating only

asked 2016-04-25 10:51:53 -0600

Urado's avatar

updated 2017-05-08 18:36:34 -0600

I found two posts on UnmetHours about this question but it doesn't help me. I want to use a LowTemperatureradiant:variableFlow without cooling. However, this object also brings a Coil:Cooling.

In this post, @MatthewSteen suggests to create an Always Off schedule and assign it to the cooling coil. But unlike the others coils (such as Coil:Heating:Water) I don't see any Availability schedule for this one: image description

The only Schedule is for control temperature in °C and does not accept a ON/OFF schedule. No more help with this answer which doesn't seem to work with OS, as pointed out by @ethankheil.

How to get rid of cooling with this object ?

edit retag flag offensive close merge delete

Comments

A quick fix waiting for a better solution.

It is possible to link the Coil:Cooling with a "fake" cooling water loop with an airflow set to 0. I have to double check if this doesn't have any impact on simulation. It adds some warnings but it seems to work as intended.

Urado's avatar Urado  ( 2016-04-25 11:09:40 -0600 )edit

2 Answers

Sort by » oldest newest most voted
3

answered 2016-04-26 05:12:54 -0600

Urado's avatar

updated 2016-04-26 05:33:11 -0600

@MatthewSteen will probably be able to confirm but the always off Schedule method is no more relevant (maybe an OpenStudio update ?).

A solution is to hard sized the maximum Cold Water Flow to 0 m^3/s and to not link the Coil:Cooling to a water loop: image description

Edit: The '0' in Hard sized has to be overwrited, else it returns to Autosized !

edit flag offensive delete link more

Comments

2

Correct, in order for the 0 to stick you must click in the field. Otherwise it will be returned to Autosized. See this GitHub issue: https://github.com/NREL/OpenStudio/is...

MatthewSteen's avatar MatthewSteen  ( 2016-04-26 06:47:39 -0600 )edit
0

answered 2018-07-12 06:19:48 -0600

SO are you succeed in modeling a radiant floor heating system? I am trying to do it, but it is very difficult, would you please share a simple example? Thank you sosososo much!

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

2 followers

Stats

Asked: 2016-04-25 10:51:53 -0600

Seen: 380 times

Last updated: Apr 26 '16