Radiant flow system with heating only
I found two posts on UnmetHours about this question but it doesn't help me. I want to use a LowTemperatureradiant:variableFlow without cooling. However, this object also brings a Coil:Cooling.
In this post, @MatthewSteen suggests to create an Always Off schedule and assign it to the cooling coil. But unlike the others coils (such as Coil:Heating:Water) I don't see any Availability schedule for this one:
The only Schedule is for control temperature in °C and does not accept a ON/OFF schedule. No more help with this answer which doesn't seem to work with OS, as pointed out by @ethankheil.
How to get rid of cooling with this object ?
A quick fix waiting for a better solution.
It is possible to link the Coil:Cooling with a "fake" cooling water loop with an airflow set to 0. I have to double check if this doesn't have any impact on simulation. It adds some warnings but it seems to work as intended.