Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

Does Rated Fan Power in EnergyPlus Include Motor Efficiency?

asked 2016-04-22 11:27:56 -0500

pflaumingo's avatar

updated 2016-04-22 11:42:53 -0500

I've been looking at the rated fan power of single speed fans (Fan:OnOff and Fan:ConstantVolume) reported by EnergyPlus and comparing it to hand calculations I've noticed that it doesn't seem to include motor efficiency. Has anyone else noticed this? Is the motor power consumption reported elsewhere? My understanding was that rated fan power should include motor efficiency.

Example: Fan efficiency = 42.75%, Pressure rise = 226.92 Pa, Flow rate = 0.090613 m^3s^-1, Motor efficiency = 85.5%

Hand calculation = 56.25 W, Hand calculation w/o motor efficiency = 48.098 W, EnergyPlus rated fan power = 48.098 W

I got the EnergyPlus value from the SQL file and the html file.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2016-04-22 11:48:36 -0500

updated 2016-04-22 11:48:54 -0500

Yes it does. The efficiency input in the fan object includes motor and fan efficiency. See the answer to Fan motor replacement savings

edit flag offensive delete link more

Comments

That's right. I was using OpenStudio and the input is labelled 'Fan Efficiency' rather than 'Fan Total Efficiency' like EnergyPlus so I mistook it for static efficiency. Just posting this comment in case anyone else interprets it the way I did.

pflaumingo's avatar pflaumingo  ( 2016-04-22 11:59:33 -0500 )edit
1

An issue has been filed to clarify this input in OpenStudio.

ericringold's avatar ericringold  ( 2016-04-22 12:13:02 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2016-04-22 11:27:56 -0500

Seen: 383 times

Last updated: Apr 22 '16