Floor area reduced when adding vertically stacked spaces into a single thermal zone

asked 2016-04-01 13:41:28 -0600

When I put two vertically stacked spaces into one thermal zone in OpenStudio. The simulation results shows that the floor area is just half of the total floor area. Even though I have checked the "Part of Total Floor Area" in OpenStudio for each space. Looks like the internal gains (people, lights, electric equipments) were defined as per floor area, so I assume in EnergyPlus simulation they are also reduced by half. Is that what's expected?

edit retag flag offensive close merge delete

2 Answers

Sort by ยป oldest newest most voted
2

answered 2016-04-01 13:54:23 -0600

updated 2016-04-01 13:55:20 -0600

I believe this is a known issue with several associated ones.

https://github.com/NREL/OpenStudio/is...

edit flag offensive delete link more
0

answered 2016-04-02 09:51:18 -0600

BL's avatar

The internal load density is not changed, but the floor area is reduced. So you need to use the multiplier in OS or E+ to recovery the actual floor area. I believe the main purpose of combine multiple zones into one is for decreasing simulation time if the loads and HVAC systems are similar between zones.