Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

Floor area reduced when adding vertically stacked spaces into a single thermal zone

asked 2016-04-01 13:41:28 -0600

When I put two vertically stacked spaces into one thermal zone in OpenStudio. The simulation results shows that the floor area is just half of the total floor area. Even though I have checked the "Part of Total Floor Area" in OpenStudio for each space. Looks like the internal gains (people, lights, electric equipments) were defined as per floor area, so I assume in EnergyPlus simulation they are also reduced by half. Is that what's expected?

edit retag flag offensive close merge delete

2 Answers

Sort by ยป oldest newest most voted
2

answered 2016-04-01 13:54:23 -0600

updated 2016-04-01 13:55:20 -0600

I believe this is a known issue with several associated ones.

https://github.com/NREL/OpenStudio/is...

edit flag offensive delete link more
0

answered 2016-04-02 09:51:18 -0600

BL's avatar

The internal load density is not changed, but the floor area is reduced. So you need to use the multiplier in OS or E+ to recovery the actual floor area. I believe the main purpose of combine multiple zones into one is for decreasing simulation time if the loads and HVAC systems are similar between zones.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2016-04-01 13:41:28 -0600

Seen: 271 times

Last updated: Apr 01 '16