Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Need some help with WaterHeater:HeatPump [closed]

asked 2016-03-30 09:23:11 -0500

Urado's avatar

I am trying to model a heating system based on an air-to-water heat pump. For this, I use the zonal object Heat Pump Water Heater and add the HPW Tank in my hot water loop. First I want to try with autosize, so I also add design days and allow sizing calculation in simulation control, as usual.

Since my heat pump works with outdoor air, I changed the following parameters :

OS:WaterHeater:HeatPump :

  • Inlet Air Configuration : OutdoorAirOnly
  • Compressor Location : Outdoor

OS:WaterHeater:Mixed :

  • Ambient Temperature Indicator : Outdoors
  • Ambient Temperature Outdoor Air Node Name : Out air node

When I run the simulation I get the following error :

* Severe * WaterHeater:Mixed = HPWH TANK: Outdoor Air Node not on OutdoorAir:NodeList or OutdoorAir:Node * ~~~ * ...Referenced Node Name=OUT AIR NODE

So, first question : How can I add this node to the list in OpenStudio ? This error is fixed if I export my model in .idf and add the node manually in EnergyPlus but then I cannot come back to OpenStudio. Do I need to write a measure ?

I also get a new error when running my simulation with EnergyPlus :

* Severe * AirLoopHVAC AIR LOOP HVAC 1 has no air flow * ~~~ * Check flow rate inputs for components in this air loop and, * ~~~ * if autosized, check Sizing:Zone and Sizing:System objects and related inputs.

This seems to be because I set the Outdoor Air Flow to 0 in DesignSpecification:OutdoorAir. If I add a value, this error disappears. However, I want the airflow rate to be autosized and I think it is possible this way (see https://unmethours.com/answers/1567/r...).

For example, it works when I use a packaged rooftop VAV so I don't understand why there is problem with this specific case. Any suggestions ?

ps : I'm using OS 1.10 and EP 8.4.

edit retag flag offensive reopen merge delete

Closed for the following reason the question is answered, right answer was accepted by Urado
close date 2016-04-01 03:50:17.993812

1 Answer

Sort by ยป oldest newest most voted
2

answered 2016-03-30 13:45:33 -0500

I think these are two independent issues. For the HPWH I think you have found a bug, because I don't think we have a test for the HPWH located outside, only inside the zone. I have filed a bug here.

For the no air flow issue, if you don't have an oa requirement then you are going to need a zone load to request flow and get things moving. Do you have a thermostat in your zone? Is there load on the zone?

edit flag offensive delete link more

Comments

Example file HeatPumpWaterHeater

WaterHeater:HeatPump:PumpedCondenser,
  OutdoorHeatPumpWaterHeater,  !- Name
  OutdoorAirOnly,          !- Inlet Air Configuration
rraustad's avatar rraustad  ( 2016-03-30 14:08:46 -0500 )edit

Thanks for your answer. Yes, obviously the two issues are independent. Usually I use EnergyPlus after creating my geometry in OS plugin for SketchUp, so I think my second problem is due to an error in my OpenSutdio model which I don't handle very well.

When exporting to idf, I see that my Heating Thermostat set in my Thermal Zone (in the HVAC Systems tab) is not translated so I probably missed something. First I have to look how to properly create a Thermostat in OS.

Urado's avatar Urado  ( 2016-03-31 04:13:02 -0500 )edit

Ok, this post could explain my problem. That should be why my thermostat is not translated when I set only heating, quite disturbing though !

Urado's avatar Urado  ( 2016-03-31 06:23:09 -0500 )edit

Careers

Question Tools

1 follower

Stats

Asked: 2016-03-30 09:23:11 -0500

Seen: 626 times

Last updated: Mar 30 '16