How to control the supply inlet temperature in IdealLoadAirSystem-object?

asked 2016-03-24 07:43:06 -0600

EnnaEnitsriK's avatar

updated 2016-03-24 08:41:22 -0600

I'm using the IdealLoadAirSystem-object in energyplus, and can see from the results, that when my internal gains increases (and I then get a cooling demand), the heating of my supply inlet temperature stops and then the room receives unheated outdoor-air e.g. at 4C.

This makes sense since IdealLoadAirObject tries to stick to the thermostat setpoint temperature (21C), but instead of decreasing the inlet temperature, I want to increase the supply air rate. How to do this? 1) Can IdealLoadAirSystem do this via specific settings, or 2) do I have to add another/new HVAC-opbejct?

The calculation is 100% thermal.

edit retag flag offensive close merge delete

Comments

Maybe I'm not reading this correctly, you want to keep the same supply temperature from heating and increase the supply air flow when there is a call for cooling?

Neal Kruis's avatar Neal Kruis  ( 2016-03-24 09:52:35 -0600 )edit

Yes, I want to keep the inlet temperature at e.g. 21C, but the amount of air coming into the room to go from e.g. 2/hr to 4/hr when a cooling load occurs. Does that make sense? :)

EnnaEnitsriK's avatar EnnaEnitsriK  ( 2016-03-25 07:54:58 -0600 )edit

1 Answer

Sort by ยป oldest newest most voted
2

answered 2016-03-25 10:09:13 -0600

Do you want the IdealLoadsAirSystem to meet the cooling load? Depending on your setpoint temperature, that may not be possible with 21 C supply air. If you want to model a dedicated outdoor air system (DOAS) that always delivers air at 21 C and has different flow rates during cooling and heating, you might need to build up an AirLoop system.

edit flag offensive delete link more

Comments

Okay, i'll try to look into making an airloop. Thanks! :) If I use OS and look at an exported idf-file from an OS-file with VAV-system, would it then be possible to know which and how many objects I need to make the air-loop correct? In your opinion :)

EnnaEnitsriK's avatar EnnaEnitsriK  ( 2016-03-26 04:27:14 -0600 )edit
1

That is a good start, though the controls for a DOAS system are going to be different. The VAV system will give you an idea of what objects are needed, but you should be able to put together a DOAS system in OS as well.

Neal Kruis's avatar Neal Kruis  ( 2016-03-28 09:33:05 -0600 )edit