How to model a (independent) heating source in EnergyPlus?

asked 2016-03-24 06:15:00 -0500

EnnaEnitsriK's avatar

updated 2016-03-27 06:42:54 -0500

In energyplus, can one add an object that simply insures that the room temperature is never below a minimum?

Like a node from which heat is flowing into the zone.. Convection, radiation, both or just one, i'm not looking for surface temperature, just room temperature.

The zoneHVACbaseboard types does not work for me..

edit retag flag offensive close merge delete

Comments

Baseboard does work?

__AmirRoth__'s avatar __AmirRoth__  ( 2016-03-24 08:43:03 -0500 )edit

Does not* sorry!!

EnnaEnitsriK's avatar EnnaEnitsriK  ( 2016-03-25 07:52:17 -0500 )edit

2 Answers

Sort by ยป oldest newest most voted
4

answered 2016-03-24 09:48:35 -0500

I think you want the Ideal Loads Air System. This object can be used to meet the setpoint of a zone without explicitly modeling any equipment.

edit flag offensive delete link more

Comments

Yes I very much want to, and I also do so. But from the results I can see operative room temperature at 20,5C e.g... which does not make sense to me...

EnnaEnitsriK's avatar EnnaEnitsriK  ( 2016-03-25 07:56:19 -0500 )edit

The setpoint will control the air temperature, not the operative temperature. If you want to control to a specified operative temperature you will have to use the ZoneControl:Thermostat:OperativeTemperature object.

Neal Kruis's avatar Neal Kruis  ( 2016-03-25 09:52:27 -0500 )edit

I'll read more about that object thanks! :)

EnnaEnitsriK's avatar EnnaEnitsriK  ( 2016-03-26 05:08:36 -0500 )edit

Hey again - I hope it's alright to come back to you with a question :) I've tried to add a ZoneControl:Thermostat:OperativeTemperature object, but I get more (1021) hours below 21 degrees then before (774).. Originally I have IdealLoadAirSystem, Thermostat, duelsetpoint, design specification outdoor air, a equipment list and the connection (referring to the objects IdealLoadAirSystem requires).. but thats all needed according to what I can read from the webpage bigladder, it says: "Zone Control:Thermostatic and related set point objects also need to be included in the input file."

EnnaEnitsriK's avatar EnnaEnitsriK  ( 2016-03-27 07:27:58 -0500 )edit

continued: Do you agree? Or did I completely misunderstand the objects way of working?

EnnaEnitsriK's avatar EnnaEnitsriK  ( 2016-03-27 07:28:40 -0500 )edit
2

answered 2016-03-24 09:51:35 -0500

You can use the OtherEquipment component (http://bigladdersoftware.com/epx/docs/8-0/input-output-reference/page-015.html#otherequipment) .

I asked for some clarification on the component in my question Clarification of EnergyPlus OtherEquipment Impact on HVAC Loads.

You could set the equipment to turn on once a setpoint condition is met like zone air temperature is below a threshold. You can also use EnergyPlus's EMS system to calculate a schedule that controls the fraction (0 to 1 of system operation) or a variable that controls the design level (how much heating provided).

edit flag offensive delete link more

Comments

Thank you for the advise and the link! I just read about "Other Equipment" in the input/output-reference, but I couldn't find a field where to define a setpoint for minimum room temperature.. Is that just me misunderstanding the object, or is that how it works?

EnnaEnitsriK's avatar EnnaEnitsriK  ( 2016-03-25 07:59:09 -0500 )edit

@EnnaEnitsriK you are correct I incorrectly described the component, I thought you could set a Control Scheme. However, you can set a schedule for the component to follow or generate a schedule with the EMS. In the EMS Applications Guide of the EnergyPlus user manuals see Example 2 and Example 5. Definitely 5.

JustinShultz's avatar JustinShultz  ( 2016-03-25 09:14:24 -0500 )edit

Alright :) thanks for answers!

EnnaEnitsriK's avatar EnnaEnitsriK  ( 2016-03-26 04:22:11 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

Stats

Asked: 2016-03-24 06:15:00 -0500

Seen: 549 times

Last updated: Mar 27 '16