The OA controller is turning off the air flow. The minimum and maximum outdoor air flow rates are autosized.
Note also that the OA controller input fields stop at the "Minimum Outdoor Air Schedule Name" field and there are more inputs that can be used to control outdoor air.
Controller:OutdoorAir,
Data Center OA Controller, !- Name
autosize, !- Minimum Outdoor Air Flow Rate {m3/s}
autosize, !- Maximum Outdoor Air Flow Rate {m3/s}
FixedMinimum, !- Minimum Limit Type
MinOA_Sched; !- Minimum Outdoor Air Schedule Name
The result of sizing the autosized inputs yields a 0 minimum (I used Miami weather so your results may be different).
Component Sizing Information, Controller:OutdoorAir, DATA CENTER OA CONTROLLER, Maximum Outdoor Air Flow Rate [m3/s], 6.83914
Component Sizing Information, Controller:OutdoorAir, DATA CENTER OA CONTROLLER, Minimum Outdoor Air Flow Rate [m3/s], 0.00000
The Minimum Outdoor Air Schedule is constant at 1, however, 1 * 0 = 0.
Schedule:Compact,
MinOA_Sched, !- Name
Fraction, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until: 24:00, !- Field 3
1; !- Field 4
If you change the OA controller inputs to place the min OA schedule name in the "Minimum Fraction of Outdoor Air Schedule Name" input field, the evap cooler will operate all year.
Controller:OutdoorAir,
Data Center OA Controller, !- Name
OARelief Node, !- Relief Air Outlet Node Name
Supply Equipment Inlet Node, !- Return Air Node Name
Unitary Package Node, !- Mixed Air Node Name
OAInlet Node, !- Actuator Node Name
autosize, !- Minimum Outdoor Air Flow Rate {m3/s}
autosize, !- Maximum Outdoor Air Flow Rate {m3/s}
DifferentialDryBulb, !- Economizer Control Type
ModulateFlow, !- Economizer Control Action Type
28, !- Economizer Maximum Limit Dry-Bulb Temperature {C}
64000, !- Economizer Maximum Limit Enthalpy {J/kg}
, !- Economizer Maximum Limit Dewpoint Temperature {C}
, !- Electronic Enthalpy Limit Curve Name
0, !- Economizer Minimum Limit Dry-Bulb Temperature {C}
NoLockout, !- Lockout Type
FixedMinimum, !- Minimum Limit Type
, !- Minimum Outdoor Air Schedule Name
MinOA_Sched; !- Minimum Fraction of Outdoor Air Schedule Name
Are you able to upload your file? or email it to me so I can review the setup.
Thank you for offering the help Sir. I will email you the file.