OS 1.10 error simulating HW Baseboard

asked 2016-03-16 09:45:33 -0500

ptruong's avatar

updated 2016-03-16 12:17:31 -0500

Hello, I am getting the following inlet/outlet node errors trying to model HW baseboard. All I have done is dragging and dropping the equipment into the zone equipment area under thermal zones. Is there something else I need to do to connect it on the plant side? Thanks

*** 536 ZoneHVAC:Baseboard:Convective:Water, *** indicated Name=HW Baseboard *** Only last 3 lines before error line shown..... *** 537 HW Baseboard, !- Name *** 538 Always On Discrete 1, !- Availability Schedule Name *** 539 , !- Inlet Node Name * Severe * IP: IDF line~539 Error detected in Object=ZONEHVAC:BASEBOARD:CONVECTIVE:WATER, name=HW BASEBOARD * ~~~ * *** IDF Context for following error/warning message: *** Note -- lines truncated at 300 characters, if necessary... *** 536 ZoneHVAC:Baseboard:Convective:Water, *** indicated Name=HW Baseboard *** Only last 4 lines before error line shown..... *** 537 HW Baseboard, !- Name *** 538 Always On Discrete 1, !- Availability Schedule Name *** 539 , !- Inlet Node Name *** 540 , !- Outlet Node Name * Severe * IP: IDF line~540 Error detected in Object=ZONEHVAC:BASEBOARD:CONVECTIVE:WATER, name=HW BASEBOARD * ~~~ * Field [Outlet Node Name] is required but was blank

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
4

answered 2016-03-16 11:23:12 -0500

Sounds like you're missing the step to connect the HW baseboard to the HW plant system.

Assuming that you've already created the HW plant system in the HVAC Systems tab of OpenStudio, follow these steps:

  1. Click on the Thermal Zones tab
  2. Click on the HW Baseboard object you assigned to the thermal zone
  3. At the right, where you can edit input fields for the object. Click on the chain link icon.
  4. Check the box next to the name of you HW plant system. This actually connects the HW baseboard to the plant, assigning the hot water inlet and outlet nodes.

image description

This same process applies to any other zone HVAC that uses chilled water as well.

edit flag offensive delete link more