Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
0

CONDENSER LOOP CHILLER WATER PLANT

asked 2016-03-12 16:09:55 -0500

HJOJOA's avatar

updated 2016-03-13 10:20:36 -0500

Hi, Running a water cooled chilled plant, the simulation run, but the cooling electrical consumption is 0, if i disconect the condenser loop and run the simulation without condenser loop, the simulation works fine, wich is the problem?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2016-03-15 09:24:52 -0500

Which modeling tool are you using? Please tag it in your question.

If you're using EnergyPlus or OpenStudio, I'm guessing that you still have Ideal Air Loads turned on. This acts like a black box attached to the zone that provides heating and cooling at perfect efficiency. Any heating or cooling required is categorized as district heating and district cooling, respectively.

To check in OpenStudio, look at the Thermal Zones tab to make sure the boxes under Turn On Ideal Air Loads is not checked (see below).

image description

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2016-03-12 16:09:55 -0500

Seen: 851 times

Last updated: Mar 15 '16