CONDENSER LOOP CHILLER WATER PLANT

asked 2016-03-12 16:09:55 -0600

HJOJOA's avatar

updated 2016-03-13 10:20:36 -0600

Hi, Running a water cooled chilled plant, the simulation run, but the cooling electrical consumption is 0, if i disconect the condenser loop and run the simulation without condenser loop, the simulation works fine, wich is the problem?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2016-03-15 09:24:52 -0600

Which modeling tool are you using? Please tag it in your question.

If you're using EnergyPlus or OpenStudio, I'm guessing that you still have Ideal Air Loads turned on. This acts like a black box attached to the zone that provides heating and cooling at perfect efficiency. Any heating or cooling required is categorized as district heating and district cooling, respectively.

To check in OpenStudio, look at the Thermal Zones tab to make sure the boxes under Turn On Ideal Air Loads is not checked (see below).

image description

edit flag offensive delete link more